I am new to the forum and would appreciate any input on this subject especially from an AHJ viewpoint:
I am contractor installing an addressable local system in a residential 4 apartment wood constructed building. My understanding is that isolation modules are required between floors to prevent a circuit fault on one floor from affecting the circuit on another floor and I would like to know if isolation modules are necessary on both the initiating and notification circuits and if so are they required at :
1.) every point where a floor transition is made on a circuit from a device on one floor to a device on another floor in the circuit (ie basement to 1st floor initiating device and back to basement initiating devices) and
2,) are IMs required when transitioning between floors only for the purpose of running conductors with no devices on the circuit of the intermediary floor (ie basement to 1st floor initiating device back to basement then to another 1st floor initiating device).
Thanks very much for any input on this subject.
Hello Tkmcnam, What is your name? What community are you in? Is it Rhode Island?
In Rhode Island, when you break the floor with the SLC you shall install an Isolation Module on one side of the circuit to isolate it for a short or failure on the other side of the circuit. When you again break the floor when leaving the floor you shall install another Isolation Module either on that floor or on the next level, before the next device. Also, if there are more than 25 devices per level there shall be Isolation Modules to separate the groups, (no more than 25 per group). If you are going up and down through floors with your SLC through-out the building, I suggest that you take another look at your design, this seems to be an inefficient way of getting the job done.
On the matter of Isolation Modules for the Notification Appliance Circuit, I suggest that you read your manual for the type of system that you are installing. I would have to say that the manual is your best friend at this point. Also, if you are going to be installing Fire Alarm Systems, you need to invest in a copy of NFPA 72, NFPA 1 & 101 wouldn't be bad either. The RI state Fire Code is readily accessible if you are conducting work in RI. In the future for bidding jobs these books would be very helpful.
P.S, don't forget to get your permits.